The sordid story:
Perimeter (baseboard) hydronic heating. Weil McClain heat/hot water furnace, Wayne M-SR burner, both about 20 years old. Annual maintenance up to date. I've added the appropriate few drops of electric motor oil to the motor oil cups each year as recommended. No problems until recently.
For the last few weeks, maybe once every day or two, I'll notice the room temp is below the thermostat setting. I go down to the basement and see the oil burner motor has popped its motor reset button on the motor housing. That also seems to have popped the burner circuit (the *red* button and warning light) on the burner control box. When this happens, the motor smells hot, and feels quite warm to the touch.
Let it cool for about 15 minutes, punch the motor reset and control box buttons back in, and all is well for a few days.
Only happens maybe once every day or two, but prior to this month never happened.
What's my next step? Is the oil burner motor on its last legs? Any test I can do?
Thanks.
Tom